    Migration from panelview 1000 to Panelview plus 7

    Hello Good Evening
    I am in need of some advice
    I am currently upgrading some of the old panelview 1000 to the latest panelview plus 7
    the files on panelview 1000 are PVA extension and when I import them into factory talk view machine edition 9.00.00 windows 7 32 bit
    I keep getting the error of PanelBuilder32 export utility is not installed. My screens also will not transfer over.
    This is my first like project

    Thanks for any help

    Eric

  2. #2
    Administrator Shawn Tierney's Avatar
    Join Date
    Sep 2016
    Location
    Berkshires, MA
    Posts
    2,415
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Thanks Thanks Given 
    25
    Thanks Thanks Received 
    9
    Thanked in
    9 Posts
    Good morning @EORTEGA,

    I have not done this in quite some time but the message appears to want you to install PanelBuilder 32 (or at least the Export Utility) onto the same PC as ViewStudio so it can import the project.

    Do you have a copy of PanelBuilder 32 you use to maintain these old panels?

    PS - this link explains how to download it:
    https://rockwellautomation.custhelp....US#__highlight

    Sincerely,

    Shawn Tierney,
    Instructor at www.TheAutomationSchool.com