    52h error on micrologix 1500

    This problem began with the system going into a fault that would not stay cleared. I am trying a new base and I have an error code 52h, "base minimum series selected in program configuration was greater than the series on the actual base'. I didn't buy the replacement but can I make it work with the PLC? I understand there are A, B, and C bases. Can they all work with my PLC module? Where do I change the configuration?

  2. #2
    Administrator Shawn Tierney's Avatar
    Join Date
    Sep 2016
    Location
    Berkshires, MA
    Posts
    2,379
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Thanks Thanks Given 
    24
    Thanks Thanks Received 
    7
    Thanked in
    7 Posts
    Good afternoon @jimmackey

    In RSLogix, open the I/O configuration and click on "Adv Config" - that's where you change the base for the 1500.

    I honestly don't think changing the series of the base will affect your code - you can basically put any letter in there and nothing changes - I think you'll find the series change on the base is just to indicate that internally it is different. With my 1500 I've never looked at it - I left it a the default of Series A.

    Hope this helps,

    Shawn Tierney,
    Instructor at www.TheAutomationSchool.com