    DF1 to Ethernet


    In today's episode of The Automation Show, I setup a 515RTAENI DF1 to Ethernet bridge from Real Time Automation.
    For more information, check...

    Click here to view the original article on The Automation Blog
    Looking for affordable automation training? If you are, check out my courses at TheAutomationSchool.com!

  2. #2
    Member LcAuto's Avatar
    Join Date
    May 2019
    Location
    Charleston, SC
    Posts
    3
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    Thanks Thanks Given 
    0
    Thanks Thanks Received 
    0
    Thanked in
    0 Posts
    Shawn,
    I have a new customer with several Allen Bradley PLC's on site. 4 are SLC 5/03, 1 is a MicroLogix 1000. The RS232 port is being used on the SLC 5/03's to connect to an HM. The DH485 port, the RJ45 port, is not used. The MicroLogix has nothing connected to the mini din 8 port. I am looking for the best option to connect all 5 to ethernet for remote access/programming. At this time we are not planning any information exchange between units but having that option in the future might be nice. I have done some Google searching and found some info on products that no longer seem to be available. Hoping you can point me in the right direction.

    Thanks in advance for the help.

    Have a great and blessed day.


    JAQ

  3. #3
    Administrator Shawn Tierney's Avatar
    Join Date
    Sep 2016
    Location
    Berkshires, MA
    Posts
    2,371
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Thanks Thanks Given 
    24
    Thanks Thanks Received 
    7
    Thanked in
    7 Posts
    Good morning @LcAuto,

    Thanks for your question.

    As you probably have found, it's not easy to find DH-485 to Ethernet converters, and every option I can think of isn't cheap :-(

    A few options that come to mind are:

    1) Put all of the SLC's (using 1747-AIC) and MicroLogix (using 1761-NET-AIC) on a shared DH-485 network (Belden 9842, 4000ft max), then use a 1756-DH485 module (with 1761-NET-AIC) to bridge the DH485 to Ethernet with a 1756-ENxx module.

    2) Assuming you can't move the HMIs to the DH-485 port, use a DF1 port splitter (1747-DPS1) on each controller and then use the above515RTAENI on each serial port.

    3) Replace the 5/03's with 5/05s, and the 1000 with an 1100.

    Might be best to talk to your local Rockwell rep,

    Hope this helps,

    Shawn Tierney,
    Instructor at www.TheAutomationSchool.com